It is currently Thu Oct 22, 2020 7:54 pm
ekstra   ara
 Post subject: Requiring PPE for racking breakers
PostPosted: Thu Oct 01, 2020 6:56 am
Can someone help me understand and relay the reasoning behind needing arc flash PPE when racking breakers in an MCC? The argument was that if the door needs to be open when racking the breaker it is obvious why you need PPE. If the door can remain closed and a breaker racked in via a small racking port, why do you need PPE when you could close the breaker without any PPE? We were just going by the table in 130.6.
 Post subject: Re: Requiring PPE for racking breakers
PostPosted: Fri Oct 02, 2020 5:35 am
I would say it's due to additional risk. As you know, the tables are risk based. For example, there is a higher risk for racking/unracking because of operator error. It is/has been the case where breakers are racked in to their final position in the closed position, drawing and arc, and...well you know the rest.
Mike
PostPosted: Fri Oct 02, 2020 3:14 pm
If an arc flash occurs, the doors may not remain closed and even if they do, energy can still be released through any hole, vent etc. The link is to a video where I have 2 arc flash tests. The second one is 18,000 amps and it blows the door open. Hope it helps give you better feel for what happens.
VIDEO: Doors Blowing Open
PostPosted: Mon Oct 05, 2020 7:15 am
Why not implement remote racking from outside the boundary?
PostPosted: Mon Oct 05, 2020 9:14 am
Yes, you wear PPE to do this process. If you watched Jim's video, you saw that the doors don't necessarily stay closed and keep an arc flash contained. How a latched door can open is another question, but they do fly open.
The question I have is how often do you do this process? Seems like racking a breaker in or out of a MCC is not a standard process. If you do this on a regular basis, I'd want to know why and is it really so important?
PostPosted: Tue Oct 06, 2020 4:06 pm
https://www.eaton.com/us/en-us/products/medium-voltage-power-distribution-control-systems/switchgear/remote-racking-and-control-options-for-metal-clad-switchgear.html