MGumbert wrote:
Strict interpretation of NFPA70E would indicate that troubleshooting 120vac circuits with the power on would be classified as HRC1. PPE for HRC1 requires long sleeve shirt, long pants (both FRC rated at 4 cal. or FRC 4 cal. coveralls over non-melting clothing), Arc-rated face shield (4 cal.), safety glasses, hearing protection, hard hat, rubber gloves with leather protectors, and leather work shoes.
Is this interpretation correct ?
Yes AND no, strict interpretation of the 70E would not allow you to do this work energized unless you meet some very specific criteria and then do a risk analysis, complete an EEWP, and wear the proper PPE, which is most likely HRC1 (Assuming you meet the criteria in the notes section of the tables)
The exception to this is voltage testing (I know you said T/S but the title of your thread says "servicing") and troubleshooting, which allows you to do it with the PPE from the tables.