ekstra   ara
 Post subject: LV CB operation
PostPosted: Tue Jun 01, 2010 9:16 am 

Joined: Tue May 18, 2010 8:20 am
Posts: 5
Location: Indianapolis, IN
I'm not using tables because I've done my calculations. At a panelboard, I've determined Ie=0.6cal/cm2 and AF boundary in the neighborhood of 12".

Can someone cite the code section which mandates any specific clothing requirements for the operation of a CB in this panelboard ?

thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 01, 2010 11:44 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
Check out:

NFPA 70E - 2008 Edition 130.3(B)(1) Incident Energy Analysis

Arc Rated FR clothing and other PPE shall be used by the employee based on the incident energy exposure...

This is based on the incident energy at the working distance which is typically 18 inches. At 18 inches you seem to have a very low incident energy which would lead to PPE category 0 <1.2 cal.cm2

It is also based on working within the Arc Flash Protection Boundary which for you is 12 inches.

Your hands will likely need protection from arc flash since they will be closer and I prefer to wear FR clothing anyway. Once you have seen even a low level arc flash, it really gets your attention.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883