 Post subject: Bus Duct clearance requirements
PostPosted: Thu Sep 09, 2010 6:26 am 

Joined: Fri Jul 30, 2010 8:37 am
Posts: 4
Does anybody know what, if any, clearance requirements are necessary around buss ducts. We have one that runs along a walkway and I want to mark the flooring for aisle space and safety.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Sep 09, 2010 6:49 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
It depends somewhat on the voltage of the busduct. For systems that operate at 600v or less use NEC article 110 section II, for greater than 600v use NEC 110 sectin III. Hope this helps.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Sep 09, 2010 7:20 am 

Joined: Fri Jul 30, 2010 8:37 am
Posts: 4
So it does fall under the same requirements as all other electrical. My next question is can the required working space be in an aisle or do they need to be seperate from eachother. If I were to come three feet from the front of the bus duct to "gaurd" the area it will not leave enough walking space in the hallway where it is running through.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Sep 09, 2010 8:09 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
JPC9397 wrote:
So it does fall under the same requirements as all other electrical. My next question is can the required working space be in an aisle or do they need to be seperate from eachother. If I were to come three feet from the front of the bus duct to "gaurd" the area it will not leave enough walking space in the hallway where it is running through.


We have always based it on the same principles as other electrical equipment. The working space can in combination with the aisleways. You might want to, however, check with the local AHJ, (electrical inspector), to get his approval.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883