wbd wrote:
Thank you but I think you missed a point in my posting. Does one need hearing protection since an analysis was done (no tables) and the AFB is 12" If one is operating a SWD breaker in a bkr panel that is 0.6 cal/cm2 at 18", the only part of your body that is within the AFB is 12" of your arm to operate the bkr. Do you need hearing protection?
What are the results of your risk analysis?
Does your ESWP included language about not needing PPE when you are outside of the AFB?
You have 'discovered' one the grey areas of NFPA70E - What PPE is required to protect a worker, when calculations have been performed.
Many, if not most, companies are reluctant to make this decision, therefore they use NFPA70E tables backwards by equating an HRC, and its PPE, with a calculated incident energy level.
This issue may get worse with the next edition of 70E.