PostPosted: Mon Feb 21, 2011 1:48 pm 
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
I remember GE Servicing our Switchgear (cleaning and checking) in the past and using protective grounding cables several years ago.

My memory is failing and I need some confirmation on the use of grounding cables for a 15KV to 480V Switchgear system.

1. We opened and locked out the poles HV switches, simple single fed system.
2. We tested to verify the 15KV system was de-energized.
3. This is the part I am vague on. I remember they GE guy attaching the cable to ground and dangling the cable near the HV Pri lead and watching it arc.
4. He did this to all three phases to remove any static charge in the line.
5. Now, would he have removed the leads from the transformer and grounded the cables? Or would he have not dis-connected the leads and grounded the transformer leads with the HV cable attached?
6. Is it proper protocol to ground the secondary also?

I cannot find a best practice for installing temp protective grounding while servicing a simple single service switchgear. Any info or reference document would be great.
Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 22, 2011 6:48 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Quote:
5. Now, would he have removed the leads from the transformer and grounded the cables? Or would he have not dis-connected the leads and grounded the transformer leads with the HV cable attached?
6. Is it proper protocol to ground the secondary also?

Temporary grounds are required when it is possible that a voltage could reappear at the point of work. If there are cables connected that can have voltage induced on them or if they could be connected to another source, then they should be grounded before working on them. This needs to be established by company safety procedures. Often procedures call for grounding all MV and HV equipment while working on it.

It is probable that once the single feed cable capacitance was discharged, no voltage could appear. If you have the temporary ground set there, I would recommend connecting it to the primary while the work is being performed, even if the cable is in a location where no voltage can be induced on it.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883