 Post subject: Visual Inspection
PostPosted: Fri Apr 08, 2011 6:32 am 

Joined: Thu Feb 24, 2011 3:36 am
Posts: 13
Hello all,

Do you need to wear Arc Flash PPE when visually inspecting a 480 volt panel open?

Another question. When changing a door on a 480 volt panel are we required to de-energize if we can.

I am pretty sure I know the answers, but just want to verify as I am new to Electrical safety and NFPA 70e.

Thank you


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Apr 10, 2011 10:05 am 

Joined: Mon Jan 10, 2011 6:34 am
Posts: 9
Location: Ohio
Yes you have to wear Arc Flash PPE when visually inspecting the 480V panel as long as you are inside the arc flash boundary with exposed, energized live conductors that have not been put into an electrically safe work condition.

As far as changing the door on a 480 volt panel while it is energized....you will have to deenergize the panel, unless deenergizing the panel would cause an increased hazard or is infeasible (doubt you can claim either case) Shut down the power (verify zero abscence in the proper manner) and then go home happy


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 11, 2011 6:07 am 

Joined: Thu Feb 24, 2011 3:36 am
Posts: 13
Thank you mvann81


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883