NFPA 70E, 110.4(A)(5): "When test instruments are used for testing the absence of voltage on conductors or circuit parts operating at 50 volts or more, the operation of the test instrument shall be verified before and after an absence of voltage test is performed."
Note also that I have found NO manufacturers that will state in writing that their non-contact voltage detectors are acceptable as devices for testing for absence of voltage below 1000 volts. Above that range, that is the tool you use (when rated for it). Below that voltage, a multimeter or an equivalent tool which accomplishes the voltage testing duty and can be tested before and after is the tool of choice. "Wiggies" are also on my ban list due to the propensity for destroying all electronic devices by means of inductive kick. In my shop, it's either a multimeter, or a multimeter except for medium or high voltage. And the multimeter must be properly rated for the transient overvoltage that can be expected (Category rating), having nothing to do with the bogus "outdoor/indoor" type ratings usually attributed to category ratings. If you do not do this and the voltage is too high or you see a transient go through the meter, it can explode and injure the electrician using it.
The reason for testing before and after is to verify operation of the meter. If there is an equivalent fail safe way to do this (I don't know of any) at the point of potential injury, then this could be an acceptable substitute for this test but you better have more than adequate documentation for what you are doing.
Quote:
Not being an electrician or skilled as a Qualified Person I need to understand how to verify zero voltage on MMCs and 480 disconnects. My dilemma involves LOTO. If a MCC or disconnect has been placed in the open position and a lock is applied, what choices are avilable to electricians or a qualified person to check for hazardous voltage?
First off, it is not ZERO voltage. It is "absence of voltage". It should be stated as absence of hazardous voltage. Generally this is attributed to meaning less than 50 volts. Especially in the case of open vacuum contactors, there is usually a little stray voltage floating around all electrical equipment and getting close to true zero voltage is only possible if you create an equipotential ground condition. This is much more critical as the system voltage goes up to the point where temporary grounds are a critical component of electrical LOTO.
There are several LOTO procedures in OSHA. Just within 1910, there is Subchapter J (familiar to most), S (electrical for utilization), R (269, electrical for distribution), and O (for production).
Quote:
I understand when there are draw out breakers but not where the door is closed. Thanks in advance for any assistance you may offer.
You must expose the wiring to test it. Simple as that. The testing process itself is done as if the equipment is energized even though it is hopefully NOT energized. You suit/glove up just as if the circuit is energized and do the test. No EEWP required because this is a task which cannot be done under safe working conditions since you can't get to a safe working condition without testing for absence of voltage. Hence one big reason for the voltage testing exception to EEWP's. With drawout breakers you are STILL required to test even though it seems like you don't have to since the line is physically disconnected. However, lots of electricians have been killed by making assumptions about how things are wired up. I've had enough "surprise" moments myself early on to be religious about test-before-touch.
The most annoying breakers are the ones with the rotary handles where you have to open the door first, and THEN attach the lock because they don't provide any means to opening or closing the door after the lock is applied. I've also banned these in new installations not only for this reason but because they bend/break with too many locks on them, and because the pin that you commonly see on some of them tends to have problems lining up with the door later on, and because the mechanism is usually not very well built. In short, get rid of these things and don't let anyone install more of them. They are nothing but trouble.
I'll give you an example of WHY you must actually test the equipment you intend to work on and not do the test somewhere else. In a mine in New Jersey I had a starter that stopped working. So I went to the disconnect and locked it out. I opened the starter up and knew that I was safe. Just as a precaution I put my meter on the starter and....voltage was present. I went back to the disconnect and opened it and found that it had actually been gutted a couple years previous, but no one had removed the labels. If I had not tested it, I would have very likely been hurt or killed. I remember this incident vividly because I actually didn't have any intention of testing it...at that moment I had second thoughts and went all the way back to my truck to get my meter to test it "just in case". It was if an angel was smiling on me that day because that little second though saved my life, and I got religion at least as far as testing for absence of voltage every time after that.
Second example: electrician goes to unwire 2 office trailers out of 3 in a mine in North Carolina. Being as all there was is a panelboard with 480 V breakers on it, he opens the two breakers, tests them at the panelboard, closes the panel door, and locked out the door. He then takes out his trusty wire cutters and begins to snip the wiring. His wire cutter welds itself to the fully live wires he was cutting into. Turns out that again, breakers were mismarked and he got "lucky" finding the mismarked breaker first.
Third example: In a foundry where we had two 2400 V to 480 V transformers in an electrical room with just the two transformers, two 2400 V disconnects, and two 480 V disconnects. Not having any 2400 V equipment, electrician went to the labelled 480 V disconnect and open this and leave the door open. Went to labelled 2400 V disconnect and open and lock this, then open the door and inspect. Then go back to the 480 V panel and check for absence of voltage. Appears dead. Then open the transformer door and begin physical inspection on transformer. Surprise! Transformer is not dead. Careful inspection reveals that both panels were mismarked and that the conduit "criss-crossed". Shortly after that, electricians got a Christmas present...2400 V testing equipment.
Fourth example: Electrician in Georgia goes to open a safety disconnect and locks it out. Electrician tests one phase but not all three. Then begins to unwire motor. Surprise! Motor is not dead. Fortunately the net effect was to destroy a screwdriver, scare the heck out of the guy, and trip the fuses. Careful inspection reveals that one of the blades in the disconnect had stuck in and thus one phase was still energized.
Fifth example: Electrician energizes main breaker on 4160 V distribution system. Electrician working on terminating some wiring on a locked out breaker fed by the main breaker gets "zapped". Turns out that especially when there is no load on the bus, vacuum breakers can easily act as voltage dividers and transfer significant voltage to otherwise "dead" wiring. Lesson here was partly use of temporary grounding but more importantly since they were changing state of the system, testing for absence of voltage should have been repeated before proceeding.
I can probably come up with a dozen of these things. It happens far too common...what you think is out there and what's really out there are two totally different things. The only defense is testing for absence of hazardous voltage.