It is currently Sat Apr 01, 2023 2:22 pm



Post new topic Reply to topic
Author Message
ekstra   ara
 Post subject: "No load" break cutouts
PostPosted: Sat May 12, 2012 9:23 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2173
Location: North Carolina
We all know that you should never, ever open a cutout under load unless it is designed with load breaking capabilities or using a portable load break device on a hot stick, but just how much current is "no load"? It is common practice for instance to ignore the core loss "load" of smaller transformers but I'm interested in exactly what the cutoff is. In our operation it appears that at 25 kV, somewhere between 1 MVA and 2.5 MVA, we opt for installing load break switches. Below that level, we never bother putting them in. Any thoughts or practical experience on the cutoff?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 15, 2012 10:13 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Even MV no-load break switches will have an interuption rating on them, usually small, 100A or so. I don't consider core loss current "load".


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat May 26, 2012 8:54 pm 
User avatar

Joined: Sun May 13, 2012 5:00 pm
Posts: 7
Location: Amarillo, Texas
Zog wrote:
Even MV no-load break switches will have an interuption rating on them, usually small, 100A or so. I don't consider core loss current "load".

I've been in the Utility business for over forty years. My experience and the practice of the company I worked for those many years was to consider any "core loss", or line charging for that matter, greater than 5 amps should require some form of load break device.

Keep in mind when you are dealing with core loss or line charging current you are approaching a PF angle of 90 degrees - leading for line charging and lagging for core loss. Either way the recovery voltage when breaking those currents is very nearly at peak value.

That said, most pole line transformers can easily be dropped with a standard cutout. Also note that I am referring to open air cutouts, not metal enclosed equipment. That's another area - one I am going to have to become very familiar with in a very short time.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883