OK..NFPA 70E 130.7 (B) (6) (a) States The PPE for Hand and Arm Shock Protection "shall be rubber insulating gloves with leather Protectors...." In NFPA 70E Table 130.7(C)(10) Hazard/risk Category 0 referances "Leather Gloves (AN) (note 2) " note 2 goes on to mention rubber gloves etc. so? are we just talking "leather Gloves" only? or leather gloves with rubber insulating gloves ? Clarification anyone


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 23, 2008 1:13 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Maughbc wrote:
OK..NFPA 70E 130.7 (B) (6) (a) States The PPE for Hand and Arm Shock Protection "shall be rubber insulating gloves with leather Protectors...."


Right, the rubber is for shock protection, the leathers are to protect the rubber from damage.

Maughbc wrote:
In NFPA 70E Table 130.7(C)(10) Hazard/risk Category 0 referances "Leather Gloves (AN) (note 2) " note 2 goes on to mention rubber gloves etc. so? are we just talking "leather Gloves" only? or leather gloves with rubber insulating gloves ? Clarification anyone



This table is for arc flash protection, not shock protection, so leathers only. Unless you cross the RAB, then you need the rubber gloves. Make sense?

P.S. Looks like you have an older version of the 70E, things are a little clearer in the new version.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883