 Post subject: IR Scanning
PostPosted: Tue Oct 28, 2008 8:12 am 

Joined: Mon Oct 29, 2007 7:33 am
Posts: 9
I have heard that there maybe a new provision in the 2009 NFPA which deals with PPE levels required for performing IR scans. Mention has been made of a "dotted line boundary" which would have a reduced level of PPE for the scanner. Is there any validity to this new rule?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 28, 2008 8:58 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
blackdog wrote:
I have heard that there maybe a new provision in the 2009 NFPA which deals with PPE levels required for performing IR scans. Mention has been made of a "dotted line boundary" which would have a reduced level of PPE for the scanner. Is there any validity to this new rule?


The tables in the 2009 70E have IR scanning listed as a task that has some reduced PPE requirements, however the person pulling the panels will still need the right PPE for that task.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 29, 2008 7:34 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
The "dotted line boundary" for infrared thermography is the Restricted Approach Boundary. The 2009 NFPA 70E has IR Thermography as:

Category 0 for 240V and below
Category 1 between 240V and 480V
Category 2 for 600V class switchgear
Category 3 for MV Switchgear through 38 kV and starters through 7.2 kV

Here's the catch:
These categories are subject to the footnotes that give maximum fault currents and clearing times so someone needs to determine these values. If you are outside these limits - time to perform detailed incident energy calculations. Also IE calcs could move you to a lower Category (or even higher)

The Restricted Approach Boundary is one of the boundaries for shock protection. You look it up in NFPA 70E. As an example 480V it is 12 inches - i.e. keep the camera back 12 inches from the live parts. This distance goes up with voltage.

I am uncertain how the short circuit and clearing time footnotes stack up with the restricted approach boundary. Normally, IE is calculated based on 18 or 36 inches from the live part. If you are 12 inches from the part (using the RAB) and there is an arc flash, it would be much worse since you are closer.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 29, 2008 5:29 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 519
Location: New England
Jim,
Couple of thought. NFPA needs to increase their time element from 2 cycles to 6 cycles min to open up the use of the table and include more installations. 2 cycles cutoff is way too limiting. 65KA is a bit on the high side, so if it helps they could reduce Ibf to 55K and still cover a much greater percentage of sites.

IR tech can always suppost their cameras off a KV rate pole so the camera goes closer and their body stays behind.

12" for the camer probably means 18" for the chest, so the IE numbers would be okay if based on 18"


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 30, 2008 3:23 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
Good point Haze - Thanks!

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883