It is currently Tue Oct 13, 2026 3:37 pm



Post new topic Reply to topic
Author Message
 Post subject: Distances between containment areas of xfmrs
PostPosted: Wed Nov 07, 2012 1:31 pm 

Joined: Thu Oct 18, 2012 11:44 am
Posts: 4
Hi All!

I am curious if anyone has any knowledge of NESC or other regulations that deal with minimum distance requirements of containment areas between transformers.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 08, 2012 6:54 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
FM Global in particular publishes guidelines on this. They like to see 25 feet minimum with flammable fluids, and then they drop to a lower number (10 feet if I recall) for less flammable fluids, unless you have a 2 hour fire barrier between transformers or some sort of fire suppression (deluge) in which case it goes to essentially zero.

The issue or concern for them is really a matter of liability...that if the containment of burning oil on a transformer fails, it overheats another one and causes it in turn to fail as well.

With dry transformers the containment is a nonissue.

Also, containment by itself generally doesn't really do a lot of good from an environmental point of view in the U.S. because it's still a spill and every time you have to drain the containment (rainwater), you have to test it to verify what it is to satisfy the regulators. So we stopped doing containment.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 12, 2012 10:30 am 

Joined: Mon Apr 18, 2011 1:43 pm
Posts: 11
Location: Denver, CO
As usual Paul's spot-on. I just thought I'd add there are a couple of companies that I know of who make the less flammable fluids - Cooper's Envirotemp FR3 and ABB's BIOTEMP. Both will require retraining on their use but, since they're plant based, are typically less hazardous to work with.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883