Post subject: MV grounding Posted: Fri Dec 14, 2012 9:12 am |
|
Joined: Thu Sep 06, 2012 10:57 am Posts: 4
|
Recently we were having some work done on controls of our MV switch gear (Russelectric). I cannot find anywhere to attach the grounding clusters. There is no accessible connection to the main bus. The only way to access make a connection would be through a breaker. Does anyone have an experience dealing with something like this? I've hear of a device we can buy that you can rack-in directly onto the bus. Thanks You
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Fri Dec 14, 2012 12:31 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
Ground and Test device. We build them and also stock plenty of OEM versions. There should be some other manufacturers breaker in the gear.
|
|