 Post subject: Verification of voltage testing device integrity
PostPosted: Tue Apr 30, 2013 4:13 am 

Joined: Wed Jan 30, 2013 5:05 am
Posts: 8
Being in the business for over 40 years, I know the answer but I wanted to get some thoughts/respnses to my discussion with a coworker. The statement was made to the effect that a qualified person could carry a 9 volt battery with them and when it came time to verify the integrity of the voltage testing device, the battery could be used. The thought being when LOTO is being performed and the last steps would be to verify the device integrity, test for zero energy and then verify the device integrity again without subjecting the worker to voltages over 50 volts.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 30, 2013 10:22 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Source used for verification needs to be on the same setting as what you are checking. If you have to switch from AC to DC voltage (Like on a fluke) then you are not validating the operation of the meter.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 30, 2013 10:25 am 

Joined: Wed Jan 30, 2013 5:05 am
Posts: 8
Zog wrote:
Source used for verification needs to be on the same setting as what you are checking. If you have to switch from AC to DC voltage (Like on a fluke) then you are not validating the operation of the meter.

What about an analog multimeter with ranges?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 30, 2013 11:45 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Monroe Charlton wrote:
What about an analog multimeter with ranges?


Same thing, must be on same scale.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 06, 2013 10:58 am 
Sparks Level

Joined: Fri May 01, 2009 9:10 am
Posts: 73
I agree Zog. I would add that OSHA only requires verification of the device if the system is >600V.


1910.333(b)(2)(iv)(B)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 06, 2013 11:13 am 

Joined: Wed Jan 30, 2013 5:05 am
Posts: 8
Viper57, you are correct about 1910 but 70E Article 110.4(A)(5) states 50 volts or more.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 07, 2013 4:24 am 

Joined: Mon Aug 03, 2009 10:22 pm
Posts: 12
Location: North Carolina
I agree. Must be on the same scale if analog meter and same type with digital multimeter. Basically, if you reposition a switch or anything else on the meter you have to redo the test.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 07, 2013 8:48 am 
Sparks Level

Joined: Mon Jun 07, 2010 9:40 am
Posts: 119
"I agree. Must be on the same scale if analog meter and same type with digital multimeter. Basically, if you reposition a switch or anything else on the meter you have to redo the test."
OK so what about an autoranging meter. :)

But more seriously, Our hotstick voltmeters are packlaged with a little battery powered inverter that genereates MV levels for the live dead live test. But a battery by itself???


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 13, 2013 9:56 am 

Joined: Fri Sep 21, 2012 8:23 am
Posts: 12
Isn't there an allowance to use a second working meter? This may not answer the question but if a team is working together and they each have a working meter then the absence of voltage can be verified. I think its in 70E but I don't have it with me to check.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 30, 2013 11:22 am 

Joined: Mon Mar 08, 2010 1:47 pm
Posts: 1
Location: Florida
KEC wrote:
Isn't there an allowance to use a second working meter? This may not answer the question but if a team is working together and they each have a working meter then the absence of voltage can be verified. I think its in 70E but I don't have it with me to check.

The purpose of the live dead live is to validate the meter is set up right and working properly to verfiy zero energy, there's no short cut to do that properly that does not increase risk.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jun 05, 2013 4:50 am 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
Why not test it on a 120 volt receptacle in the room? Then you are measuring AC.. Test before and after you verify your isolation...


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883