| Author: | Tim O [ Wed Jun 05, 2013 5:24 am ] |
| Post subject: | Lock out - Tag Out |
My company's written policy is for everything to be locked out and tagged out before working on a piece of equipment. No one is permitted to work on anything energized. Will we still need to do an arc flash hazard analysis or will generic labels be enough? |
|
| Author: | stevenal [ Thu Jun 06, 2013 9:00 am ] |
| Post subject: | |
What does your generic label say about PPE? Will you know what PPE to wear when verifying deenergization? |
|
| Author: | A King [ Fri Jun 07, 2013 8:47 am ] |
| Post subject: | |
It's not locked out until it has been verified as de-energized, and proper PPE is required for voltage testing (even testing for the absence of voltage). Also, what about troubleshooting? |
|
| Author: | elihuiv [ Mon Jun 10, 2013 6:59 am ] |
| Post subject: | |
This is a common claim. We don't do ANY live work but the two above examples are common everywhere. You must deal with these. Another common mistake is that we do not allow work >40 cal when you have hazards >40 cal you will allow some type of "work" in the form of testing or grounding or both. |
|
| Author: | Steve Hudgik [ Mon Jun 17, 2013 6:19 am ] |
| Post subject: | |
The above examples are good. In addition, you cannot tell what situations will come up in the future, or how things will change, or what mistakes people will make. So NFPA 70E does not saying labeling is required, except... (There is no "except.") The bottom line is that correct, accurate labeling is required. |
|