 Post subject: connecting the remote racking device
PostPosted: Tue Dec 16, 2014 1:20 pm 

Joined: Tue Sep 17, 2013 7:35 am
Posts: 17
We are trying to develop work rules to address utilizing our newly purchased Remote Racking devices. When connecting the remote racking device to the MV breaker, do you require Arc Flash PPE?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: connecting the remote racking device
PostPosted: Thu Dec 18, 2014 9:29 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2173
Location: North Carolina
Not unless it is armed and could rack it in/out. Generically, 70E-2015 states that opening/closing doors requires arc flash PPE. OSHA has investigated cases of arc flash while opening doors. However every case involved exposed energized conductors (not just control circuits) behind the door and either a foreign object such as a screwdriver or in one case a loose sheet metal panel from a previous incorrect repair that fell into exposed bus. I am unaware of a case where exposed bus was not a necessary precondition. With most switchgear breakers the only exposed components are control wiring, which is notoriously exposed but cannot sustain an arc sufficient to cause an arc flash over 1.2 cal/cm2.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883