Voltrael wrote:
If a breaker trips in my home do I need to open up the covers on the circuit panel and inspect that breaker for damage? Do I need to call in an electrician to do that for me?
Not unless you are on the job...OSHA doesn't apply!
UL 489 molded case breakers (to say nothing of their ANSI counterparts) are only rated for somewhere between 2-3 and 50 interruptions at full ratings and several thousand at no-load conditions. Opening under a fault is the highest stress the breaker will see in operation. So the odds are not good when it comes to operating a breaker after a fault.
That being said, NEMA AB-4 is available for FREE from
www.nema.org. It's a free download. There are less than a handful of standards that NEMA publishes that are actually free so that's the reason I mention it. I suggest reading it first.
In short NEMA AB-4 requires the following:
1. A visual inspection after every TRIP. It takes roughly 10 seconds to do this. The standard has nice color pictures of what to look for. Most of the more extensive inspections only occur if the first 10 second look finds anything. The reason that lighting panels are such a problem is that to follow NEMA AB-4 correctly you really need to inspect the breaker terminals and the casing. In a live front panel or an MCC (if the remote operator doesn't fully enclose everything) this is easy. In a dead front panel, it's just not possible short of taking the panel apart. So far I've been using the direction of "look at what you can see". This really isn't compliant but I'm at a loss as to what else to do. Ultimately perhaps the best option is to use lexan or lucite covers but if we go there, then we need to get serious about dust/contamination ratings for lighting panels as well, most of which are just plain terrible even if they have some kind of NEMA rating higher than 1.
2. Exercise the breakers once a year. Based on what I know from a reliability point of view the NFPA 70B requirement which is every 3-5 years for continuous operation is probably more appropriate.
3. PERIODICALLY do the visual inspection and do some sort of testing to verify that everything is working properly, but NEMA AB-4 is pretty vague on how often (if ever) this has to be done. My own perspective is this:
A. If the breaker is "large" (800 A frame or larger) there is evidence (IEEE Gold book) that the failure rate is about 3 times higher than small breakers. So we need to do these ones.
B. If the breaker is "critical" such as protecting a fire panel or some other safety/critical equipment then subject it to the full test.
C. Related to B, if the breaker is what controls the incident energy for equipment that is routinely worked on, then again it must be selected for periodic testing.
D. Otherwise in reality its not "critical" equipment. So like every breaker in the lighting panel in your house, run to failure.