wilhendrix wrote:
What other PPE is TM wearing - No arc flash equipment but they do wear gloves and leather covers as well as safety glasses, ear protection and cotton work long sleeves shirts and long pants made with cotton.
This is rated up to 1.2 cal/cm2 for incident energy. Untreated cotton can catch fire and cause a severe burn. Unlike with welding an arc flash happens so fast that the victim will NOT have time to get away. There are fire retardant versions (called arc rated) of shirts and pants that are treated cotton that are rated from about 6 cal/cm2 all the way to 12 cal/cm2. This is basically the same thing as a "welders" shirt and pants except that the material has been tested with a simulated arc to verify the maximum thermal energy that it can withstand while still providing adequate protection to the worker. Since this is a welding shop anyways if you just switch to those for shirts and pants it will work for both purposes.
I have personally "tested" these against welding slag. They do burn but they don't sustain a flame so you just get holes where the molten metal burned through.
Quote:
Is an electrical hazard label located on said disconnect? Not an arc flash label, just the factory label that came with the disconnect plus a voltage label that was added by the plant.
Arc flash label is required by National Electrical Code as of 2002. OSHA cited General Motors for this I think around 2008. The manufacturers DO not apply this label and you can't get them to do it. The issue is that the required label depends on the current available from the upstream power source which is site specific. So the end user is required to put these labels on.
Quote:
Are the supply side terminals covered or could they be an old type disconnect that leave exposed wires and lugs? There are a variety of older and new disconnects. Most have barriers, but I think a few don't have barriers.
Barriers don't matter except in that they may change the equipment from not exposed to exposed wiring which then mandates shock protection PPE. This is somewhat independent of arc flash concerns. Since you've got to get at the lugs at some point all that it changes is whether or not opening the doors exposes anything and makes opening the door itself potentially hazardous.
Quote:
Is this just a Lock out(control of hazardous energy)? Yes, and even though no one else gets into the disconnects, they still apply their own lock.
OSHA has about a dozen different "LOTO" procedures. They are all similar but not exactly identical. Be aware that in the case being discussed there are three to be aware of : Subchapter J, Subchapter O, and Subchapter S. This is different from construction (1926) and generation/transmission/distribution (Subchapter R, multiple sections).
Subchapter J is the "general" or "mechanical" LOTO. This would be used for instance if you locked out a ventilation fan to work on the fan shroud. It is the one that is most familiar to most people and can be used in lieu of Subchapter O but is specifically prohibited to be used as a replacement for Subchapter S.
Subchapter O is for minor servicing and adjustment, generally a "production" lockout. It doesn't require locks at all...just that there is a written procedure that is followed. This would be the case for instance when someone shuts off a welder to reposition a work piece. No lockout is typically used for this activity.
Subchapter S is for electrical work. It is nearly identical to Subchapter J except that all the workers doing this work need to be qualified workers, a test for absence of voltage is required, and in some cases personal protective grounding is required.
Quote:
Is the TM using a properly rated meter(Cat Level)? Yes, they do use good quality Fluke meters.
The brand name is immaterial. Fluke makes meters that are NOT rated for the service and older meters (more than about 10-15 years old) weren't rated for a specific category anyways. Depending on what you are doing typically you would need either a CAT III or CAT IV meter and these are subdivided by voltage. For industrial 480 V systems I recommend using either CAT III/1000 V or CAT IV/600 V meters. These are the highest rating available and even though the specifications look different they have exactly the same test requirements. The "category" rating by itself is some kind of meaningless confusing terminology when in reality the key is the transient test that the meter is designed to withstand.
If you get this wrong if a transient (voltage surge) occurs while the probes are on the wires the meter can start an arc flash and explode causing major injuries to the person using the meter. It is rare that this happens but most larger plants had about one incident every 10 years or so up until the category rating system came along.