| Phase swapping in 13.8 kV cabinet https://brainfiller.com/arcflashforum/viewtopic.php?f=10&t=5301 |
Page 1 of 1 |
| Author: | Kenneth Sellars [ Wed May 06, 2020 7:40 am ] |
| Post subject: | Phase swapping in 13.8 kV cabinet |
Just curios what the group's thoughts are on this one: An electrician during a utility switchyard construction project (energized yard with a section being replaced) notices that a 13.8 kV indoor cabinet has A and C phases backwards according to the design. After a lengthy discussion, and due to some verifiable operational limitations, a decision is made to lockout and verify the upstream VCB, and not hang grounds. The electrician enters the cabinet with voltage-rated gloves, arc flash clothing, no sleeves, no hardhat/faceshield, and lifts the shields from the cables, and shorts each phase to ground to "discharge any static charge." He then proceeds to swap the phases with no issues. What would you say in that scenario if you were informed after the job had been completed? |
| Author: | wbd [ Fri May 08, 2020 6:12 am ] |
| Post subject: | Re: Phase swapping in 13.8 kV cabinet |
The utility I used to work for never would have allowed that. Grounds needed to be hung, visible breaks on both sides and test for de-energized prior to working. |
| Author: | Kenneth Sellars [ Sat May 09, 2020 4:18 am ] |
I received a call after this happened and the utility wanted my opinion. I’m with you - I’ve never seen a utility allow work like this without grounds applied, and usually it’s required to form a local equalized potential zone. The reason the contractor gave was downtime limitations on the upstream transformer that could have a detrimental effects on the grid. Obviously OSHA allows utility energized work - it happens often, but the requirements greatly increase when doing so. Just curious what this group thinks about it. Thanks for your reply! |
| Author: | wbd [ Sun May 10, 2020 10:05 am ] |
The utilities I worked for would require that the work be considered energized work if no grounds were applied, even if there are visible breaks and the circuit tested dead. All energized work procedures would have to be followed. Typically this extends the down time. |
| Author: | Flash [ Mon Jun 01, 2020 1:27 pm ] |
What was the actual concern, metering? Kenneth Sellars wrote: Just curios what the group's thoughts are on this one:
