 Post subject: Exposed Metal Parts Within Panels
PostPosted: Wed Dec 11, 2024 8:48 am 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 52
Location: Sioux Falls, SD
Recently I have observed multiple panelboard installations at different facilities in which the studs used to wall mount the panel are not protected. These studs extend well within the panel and conductors route against them which is not appropriate. In most instances I see red rubber caps installed over the studs to guard against this. Is this specifically called out in the NEC or in any UL standard for the construction of panels?


Attachments:
panel stud.jpg
panel stud.jpg [ 112.74 KiB | Viewed 884 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Exposed Metal Parts Within Panels
PostPosted: Thu Dec 12, 2024 8:20 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 133
Check out NEC 312.10.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Exposed Metal Parts Within Panels
PostPosted: Fri Dec 13, 2024 11:23 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 588
Location: Wisconsin
The factory mounting studs are not prohibited by the equipment listing standards.
This is an installation issue, where the qualified installer should know that abrasion protection must be added as needed.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883