I had a contractor working with this PPE on a switchgear, can you help me to point out what's wrong here ?


Attachments:
unnamed (1).jpg
unnamed (1).jpg [ 1.27 MiB | Viewed 1439479 times ]
unnamed.jpg
unnamed.jpg [ 1.19 MiB | Viewed 1439479 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for switchgear
PostPosted: Mon Dec 18, 2023 1:39 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Is the equipment labeled with a current IE value or PPE level and has the equipment been maintained?

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for switchgear
PostPosted: Mon Dec 18, 2023 11:56 pm 

Joined: Wed Dec 12, 2018 12:59 am
Posts: 12
Location: Germany
Nice, can I get a quote on this 40 cal Jeans and sweatshirt? Seems more comfortable than the usual suit :)
Also those test leads dont seem like they are Cat. IV


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for switchgear
PostPosted: Tue Dec 19, 2023 10:50 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 617
Location: Wisconsin
Without knowing the available incident energy you cannot say anything is wrong.

I know plenty of people, including myself, that prefer to put my whole "Cat 4" hood on rather than wear a balaclava. Also having to carry another face shield with a lower rating on an airplane when I travel is a pain. Jeans and sweatshirt are readily available up to "10 cal".


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for switchgear
PostPosted: Tue Dec 19, 2023 11:11 am 

Joined: Wed Dec 12, 2018 12:59 am
Posts: 12
Location: Germany
It's a bit hard to read because it's so small but I think the label in the first picture says 34.6 cal/cm²


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for switchgear
PostPosted: Thu Dec 21, 2023 8:33 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 617
Location: Wisconsin
MarkusK wrote:
It's a bit hard to read because it's so small but I think the label in the first picture says 34.6 cal/cm²


Which may be true for the line/load lug compartment at the back of this switchgear. however, it may not be applicable to a low voltage/instrument compartment where the worker is.

Just not enough data to say the picture shows a dangerous activity.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883