PAult
|
Post subject: When Are V-rated Tools needed Posted: Tue Nov 24, 2009 8:14 am |
|
Joined: Wed Oct 29, 2008 6:05 am Posts: 39
|
When working within which boundry are V-rated tools needed? LAB or RAB, I have conflicting information.
Thanks
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Tue Nov 24, 2009 10:07 am |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
pault wrote: when working within which boundry are v-rated tools needed? Lab or rab, i have conflicting information.
Thanks
lab, 130(d)(1)
|
|
Top |
|
 |
PAult
|
Post subject: Posted: Tue Nov 24, 2009 10:13 am |
|
Joined: Wed Oct 29, 2008 6:05 am Posts: 39
|
Zog wrote: lab, 130(d)(1)
Thanks!!! Thats what I thought but some training showed the RAB.
|
|
Top |
|
 |
elihuiv
|
Post subject: Posted: Tue Nov 24, 2009 10:47 am |
|
Sparks Level |
 |
Joined: Sun Jan 04, 2009 5:00 pm Posts: 288 Location: Louisville, KY
|
Insulated Tools
The NFPA 70E standard is very clear. It is LAB but OSHA is unclear. OSHA says, "working near" but leaves this undefined. NFPA 70E used to define working near in 2004 as LAB but dropped the definition for various reasons leaving insulated tools at LAB.
|
|
Top |
|
 |
viper57
|
Post subject: Posted: Sun Dec 13, 2009 5:40 am |
|
Joined: Fri May 01, 2009 9:10 am Posts: 73
|
130.2(c)
What am I missing when I read 130.2(C) which states:
No qualified person may take any conductive object closer to exposed energized electrical conductors or circuit parts operating at 50 volts or more than the Restricted Approach Boundary set forth in Table 130.2(C), unless any of the following apply:...
|
|
Top |
|
 |
Jim Phillips (brainfiller)
|
Post subject: Posted: Sun Dec 13, 2009 12:09 pm |
|
Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1702 Location: Scottsdale, Arizona
|
You are not missing anything. What you picked up on is the source of some of the confusion.
130.2(C) says you cannot take a conducting object closer than the "Restricted Approach Boundary" which is 12 inches at 480 Volts
yet the following article states:
130.7(16)(D)(1) says use insulated tools and handling equipment when working within the "Limited Approach Boundary" which is 42 inches at 480 Volts
So if I have a conducting "object" I can get as close as 12 inches at 480 Volts but if I have a conducting "Tool" I can get no closer than 42 inches. 
_________________ Jim Phillips, P.E. Brainfiller.com
|
|
Top |
|
 |
ChevsMark
|
Post subject: Posted: Thu Jan 07, 2010 8:27 am |
|
Joined: Thu Jan 07, 2010 6:42 am Posts: 35 Location: Bowling Green, KY
|
It is confusing, we train that if testing under power, PPE and Insulated tools must be used for any testing over 50 volts. The PPE (8 cal/cm² clothing with long sleeved shirts and pants, along with insulating gloves with leather protectors) is required the minute one is opening the door which is inside the LAB and close to the RAP. The PAB is considered to be the same as touching...
|
|
Top |
|
 |
Terry Becker
|
Post subject: Posted: Thu Feb 11, 2010 11:18 pm |
|
Joined: Sun Sep 23, 2007 5:00 pm Posts: 141 Location: Calgary, Alberta, Canada
|
LogicIf we think about this from the stand point of logical, if I know I am going to interacting with the energized electrical equipment with a hand tool I will have the insulated hand tool in my hand immediately when I take it out of my insulated hand tool pouch/wrap whether I am inside the Limited Approach Boundary or not.
Terry Becker, P.Eng.
ESPS Electrical Safety Program Solutions INC.
terry.becker@espsi.ca
403-465-3777
|
|
Top |
|
 |
viper57
|
Post subject: Posted: Sat Feb 13, 2010 5:45 am |
|
Joined: Fri May 01, 2009 9:10 am Posts: 73
|
Logic?Too bad LOGIC and CODE don't always coincide! 
|
|
Top |
|
 |
jghrist
|
Post subject: Posted: Mon Feb 15, 2010 8:33 am |
|
Joined: Wed Jun 04, 2008 9:17 am Posts: 428 Location: Spartanburg, South Carolina
|
I would interprete this to mean that you could use an insulated tool to take a conductive object between the RAB and the LAB. You could use insulated pliers to hold a wire 14" from an energized 480V bus.
|
|
Top |
|
 |
Sparkytrician
|
Post subject: Posted: Mon Feb 15, 2010 3:31 pm |
|
Joined: Wed Jan 20, 2010 4:08 am Posts: 14
|
jghrist wrote: You could use insulated pliers to hold a wire 14" from an energized 480V bus.
But why would you want to just hold a wire in that scenario?
|
|
Top |
|
 |
|