 Post subject: When Are V-rated Tools needed
PostPosted: Tue Nov 24, 2009 8:14 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 39
When working within which boundry are V-rated tools needed? LAB or RAB, I have conflicting information.

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 24, 2009 10:07 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
pault wrote:
when working within which boundry are v-rated tools needed? Lab or rab, i have conflicting information.

Thanks


lab, 130(d)(1)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 24, 2009 10:13 am 

Joined: Wed Oct 29, 2008 6:05 am
Posts: 39
Zog wrote:
lab, 130(d)(1)


Thanks!!! Thats what I thought but some training showed the RAB.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 24, 2009 10:47 am 
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 288
Location: Louisville, KY
Insulated Tools

The NFPA 70E standard is very clear. It is LAB but OSHA is unclear. OSHA says, "working near" but leaves this undefined. NFPA 70E used to define working near in 2004 as LAB but dropped the definition for various reasons leaving insulated tools at LAB.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Dec 13, 2009 5:40 am 
Sparks Level

Joined: Fri May 01, 2009 9:10 am
Posts: 73
130.2(c)

What am I missing when I read 130.2(C) which states:

No qualified person may take any conductive object closer to exposed energized electrical conductors or circuit parts operating at 50 volts or more than the Restricted Approach Boundary set forth in Table 130.2(C), unless any of the following apply:...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Dec 13, 2009 12:09 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
You are not missing anything. What you picked up on is the source of some of the confusion.

130.2(C) says you cannot take a conducting object closer than the "Restricted Approach Boundary" which is 12 inches at 480 Volts

yet the following article states:

130.7(16)(D)(1) says use insulated tools and handling equipment when working within the "Limited Approach Boundary" which is 42 inches at 480 Volts

So if I have a conducting "object" I can get as close as 12 inches at 480 Volts but if I have a conducting "Tool" I can get no closer than 42 inches. :eek:

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jan 07, 2010 8:27 am 

Joined: Thu Jan 07, 2010 6:42 am
Posts: 35
Location: Bowling Green, KY
It is confusing, we train that if testing under power, PPE and Insulated tools must be used for any testing over 50 volts. The PPE (8 cal/cm² clothing with long sleeved shirts and pants, along with insulating gloves with leather protectors) is required the minute one is opening the door which is inside the LAB and close to the RAP. The PAB is considered to be the same as touching...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 11, 2010 11:18 pm 
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 141
Location: Calgary, Alberta, Canada
Logic

If we think about this from the stand point of logical, if I know I am going to interacting with the energized electrical equipment with a hand tool I will have the insulated hand tool in my hand immediately when I take it out of my insulated hand tool pouch/wrap whether I am inside the Limited Approach Boundary or not.

Terry Becker, P.Eng.
ESPS Electrical Safety Program Solutions INC.
terry.becker@espsi.ca
403-465-3777


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 13, 2010 5:45 am 
Sparks Level

Joined: Fri May 01, 2009 9:10 am
Posts: 73
Logic?

Too bad LOGIC and CODE don't always coincide! :D


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 15, 2010 8:33 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
I would interprete this to mean that you could use an insulated tool to take a conductive object between the RAB and the LAB. You could use insulated pliers to hold a wire 14" from an energized 480V bus.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 15, 2010 3:31 pm 

Joined: Wed Jan 20, 2010 4:08 am
Posts: 14
jghrist wrote:
You could use insulated pliers to hold a wire 14" from an energized 480V bus.


But why would you want to just hold a wire in that scenario?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883