It is currently Wed Oct 28, 2026 1:53 pm



Post new topic Reply to topic
Author Message
 Post subject: Arc Flash Barrier
PostPosted: Thu Jul 08, 2010 12:10 pm 

Joined: Wed Oct 01, 2008 6:05 am
Posts: 27
We have some indoor transformers with exposed conductors (both primary and secondary). The arc flash ratings are "extreme danger" on the secondary side. Although I know there's no PPE available for "extreme danger" are there any arc flash barriers that would protect people at all?
As it is, no one can enter the room with these exposed conductors. Any suggestions? Thanks!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Aug 24, 2010 6:52 am 

Joined: Thu Jan 07, 2010 6:42 am
Posts: 35
Location: Bowling Green, KY
Other than a locked door with limited access to keys (Qualified personnel only) I can't see anything unless you care to add additional fencing/gate further limiting access, and appropriate signage. But then you do not state the voltage for the primary or secondary, so it's a crap shoot.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Aug 24, 2010 7:56 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 617
Location: Wisconsin
What working distance was used in the calculations? It is possible that a 'fence' could be installed to limit the approach to a distance that may lower the incident energy to a level for which PPE exists.

What other formula parameters were used to determine the incident energy? This sounds like the bus spacing may be like 'open-air', but any arc will definitely be occurring 'in a box'.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883