smann7685 wrote:
Are there standards for enclosures that determine their capability to withstand an arc flash event of a given magnitude? I have customers asking for "enclosure arc flash rating" and have been told there are tests for enclosures, but I can't identify the standard, spec, or test procedure. Just how rugged must an enclosure be and how must it deal with the pressure for an arc flash event? We're working at 690VAC in the several megawatt power electronic conversion world. We've been through the 70E training and personnel protection exercise. We've designed in the current limiting devices. We've even experienced a couple of arc flashes during produce development. Our enclosures contained everything fine, how do I prove it to a customer?
See C37.20.7-2007
IEEE Guide for Testing Metal-Enclosed Switchgear Rated Up to 38 kV for Internal Arcing Faults
Revision of IEEE Std C37.20.7-2001. A procedure for testing and evaluating the performance of metal-enclosed switchgear for internal arcing faults is covered. A method of identifying the capabilities of this equipment is given. Service conditions, installation, and application of equipment are also discussed.