Who can install the AC Pro arc reduction switch or similar technology in Cleveland, OH? What is the advantage of this over in line fuses or breakers?
You can install them yourself or pretty much any local circuit breaker maintenance shop is probably familiar with them and can do it. The kit that it comes with is outstanding in this regard as it is very comprehensive (comes with shims, detailed instructions, mounting brackets, etc.).
Let's be clear what we are talking about though. An AC Pro trip unit is just that...a trip unit. It is sold by Utility Relay Company. You can get full documentation on their web site. What you do is take an old circuit breaker, clean it up, install new CT's and a microprocessor trip relay onto it. This replaces your old trip unit, including Digitrips.
The advantage of this particular trip unit is that it is very fast relative to electromechanical technology, much more adjustable than the Digitrip (very useful for difficult coordination problems), very easy to set up, the display doesn't go bad over the years like the Digitrips do, and it comes with pretty much every "bell and whistle" as a complete system. For instance it has Modbus communication built in if you want to connect it to your SCADA system for remote monitoring and diagnostics.
The underlying physical breaker mechanism remains the same though. So whatever the mechanical opening/closing time is, and any mechanical problems with it, remains unchanged.
Compared to an electromechanical trip unit or a fuse, it is much more accurate and usually a good deal faster than the original trip unit. Compared to the Digitrip it's probably about the same...you are simply limited by circuit breaker speed. Compared to a fuse which trips in 1/4 cycle, your limiting factor is the speed of the breaker itself. You are trading very good adjustability and capability to coordinate with the loss in speed. There are also some obvious heat dissipation advantages of electronic trip units (basically, no heaters) vs. both fuses and electromechanical trip units.
The "maintenance switch" thing is something of a gimmick that the Digitrip can't do but most modern trip relays can do. You can have multiple trip curves which are push button selectable. So many plants are putting instantaneous trips on a selector switch. With instantaneous tripping off (or delayed...basically an ST-only curve), you get your normal, well coordinated system. With the switch on, you ruin coordination but set the breaker to trip as fast as possible with a very low setting so that in the event that an arcing fault occurs, the breaker goes into instantaneous trip mode and opens as quickly as possible. Often this is the difference between <4 cal/cm^2 and 30+ cal/cm^2.