What do you think of this? 9500A with safety glasses only.

https://www.youtube.com/watch?v=CkqdzyQ0350


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Tue May 21, 2019 11:56 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 397
Location: Indiana
I'd trust those breakers before I'd trust this window film like these guys are:

https://www.youtube.com/watch?v=bAiD2VKh8z8

Thanks for sharing.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Tue May 21, 2019 12:01 pm 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 397
Location: Indiana
I'll have to see if those are in the latest SKM library.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Wed May 22, 2019 6:47 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1725
Location: Scottsdale, Arizona
stevenal wrote:
What do you think of this? 9500A with safety glasses only.

https://www.youtube.com/watch?v=CkqdzyQ0350


I would be very curious about the clearing time of this device. With no spark it seems clearing would have to be pretty close to T=0. Even very fast current limiting fuses allow some current and resulting incident energy.

Also wonder what the upper limit of available short circuit current would be - i.e. device interrupting rating.

Thanks for sharing!

Other's thoughts?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Wed May 22, 2019 9:20 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 624
From their website:

3 uS and 100 kA.

That's 1/5556 Cycles at 60 Hz by my math. Even if they can really sample that fast (I don't see a sampling rate), I'm not sure that fault current looks much different from load in that time.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Tue Jun 11, 2019 5:54 pm 
User avatar

Joined: Mon Jun 11, 2018 12:02 pm
Posts: 22
Location: Slave Lake, Alberta
The other question is leakage current. Are they rated as isolation devices or is a separate disconnect required for isolation? Since they have semiconductor in series with contact (air gap) what is the method to prove that the air gap is actually open and effective?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Digital Circuit breaker
PostPosted: Wed Oct 30, 2019 1:59 pm 

Joined: Tue Oct 29, 2019 6:23 am
Posts: 19
SS devices are very fast. Certainly under 1/2 cycle and potential under a millisecond. The main source of time is sensing and the decision making required to cause a trip not the clearing itself. I know of MEMS technology that can interrupt, for all intends and purposes, an infinite amount of prospective short circuit amperes (AC or DC) in microseconds... it has to do it that fast. As you get to these alternate technologies the rules are different!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883