wilhendrix wrote:
We recently did an arc flash study on a new Siemens 3000 amp 480 volt system. The switchboard came with Siemens’ new Dynamic Arc Reduction system preinstalled. The sort of thumbnail version of what the DAS does is to reset the main breaker so it trips at a much reduced current and time. I asked Siemens representatives this question: if there’s a short at the line side of the main breaker, what does the DAS do? Here is my concern. An electrician decides to open the cabinet and do some testing with the gear left on. He switches on the DAS and assumes he can now wear very low calorie PPE instead of 100 calorie PPE the line side has. He relies on the DAS to greatly reduce the hazard, but there is a line side fault at the main. I doubt this specific scenario may happen, but it is still possible. I’d appreciate your thoughts on this considering the fact that switchboards have few if any internal barriers to slow or stop an arc.
This is a safety training issue. A qualified person would no the zone of protection of the "DAS".
Additional signage/warning labels may be of help.
Training should also emphasis that PPE is the
last level of protection. PPE does not guarantee no injuries, only that the injuries received are not likely to be fatal.