Does anyone know of a device for remote operation of pringle switches?

We have a customer with 6 pringle switches tied to a ring bus from their incoming transformers vault that splits power throughout the site. These switches are just a hair over 40 cal at 18". Normally we would fabricate an extension piece at a right angle to the handle to increase working distance and get down to HRC 4 but there are space restrictions.

I have seen products like the chicken switch for pistol grip operation, or remote operators for LimitAmp style starters but nothing for pringle switches. Is anyone aware of such a device?

FEC2


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 26, 2010 6:33 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
FEC2 wrote:
Does anyone know of a device for remote operation of pringle switches?

We have a customer with 6 pringle switches tied to a ring bus from their incoming transformers vault that splits power throughout the site. These switches are just a hair over 40 cal at 18". Normally we would fabricate an extension piece at a right angle to the handle to increase working distance and get down to HRC 4 but there are space restrictions.

I have seen products like the chicken switch for pistol grip operation, or remote operators for LimitAmp style starters but nothing for pringle switches. Is anyone aware of such a device?

FEC2



Yes, CBS arc safe makes them. http://www.cbsarcsafe.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 06, 2010 1:07 pm 

Joined: Wed Jun 24, 2009 8:47 am
Posts: 25
Location: Canfield, OH
Zog, thanks for the tip. CBS has designed such a remote switch to work on a pringle but has not manufactured any yet. It is cheaper than going to say a static trip breaker but costlier than fabricating your own extender bar when all you need is 6-12 inches to get below 40 cal/cm2. In a case like I described earlier, the cbs switch makes a lot of sense (many swithces on site, high energy...)

We run into a lot of situations where a customer has something like a 2500 kVA transformer feeding a set of 3000A Class L fuses at 480V for their main gear. Often the available fault current and the fuse melt curve align so that even the sub-fuse or breakers are above 40 cal. What are people hearing out there from equipment manufacturers for more cost effective retrofits (i.e. arc flash relays, new fuse technology...)?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Apr 25, 2010 8:59 am 

Joined: Mon Dec 29, 2008 9:05 am
Posts: 7
Why not contact Eaton (Pringle) and see if you can purchase an electric operator for your switch. Swap out the existing operator with an electric operator. Pringle was always pretty consistent with their designs.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 26, 2010 9:40 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
FEC2 wrote:
Zog, thanks for the tip. CBS has designed such a remote switch to work on a pringle but has not manufactured any yet. It is cheaper than going to say a static trip breaker but costlier than fabricating your own extender bar when all you need is 6-12 inches to get below 40 cal/cm2. In a case like I described earlier, the cbs switch makes a lot of sense (many swithces on site, high energy...)


Just adding an extension to get it below 40cal is not my idea of mitigation, the worker is still suited up a 40 cal suit and in the flash protection boundary. Better to do it right and be outside the FPB. The arc safe people can have something like this developed and produced in a few weeks.

FEC2 wrote:
We run into a lot of situations where a customer has something like a 2500 kVA transformer feeding a set of 3000A Class L fuses at 480V for their main gear. Often the available fault current and the fuse melt curve align so that even the sub-fuse or breakers are above 40 cal. What are people hearing out there from equipment manufacturers for more cost effective retrofits (i.e. arc flash relays, new fuse technology...)?
There may be better solutions for mitigation but I don't know the details of your system, but experminting with some different fuses can make a huge difference.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 26, 2010 9:42 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
dpmac wrote:
Why not contact Eaton (Pringle) and see if you can purchase an electric operator for your switch. Swap out the existing operator with an electric operator. Pringle was always pretty consistent with their designs.


I thought about this too but he has 6 of them so upgrading all 6 may be costly. Good idea though, we upgrade these all the time, pringles are a little more involved than say a boltswitch but can be done if you know the equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 29, 2010 8:23 pm 

Joined: Thu Apr 29, 2010 5:50 pm
Posts: 4
Location: Michigan
*Disclaimer* I work for Eaton.

We also offer a remote racking system (just grabbed this off of Google) - http://www.eei.org/meetings/Meeting%20Documents/2009FallTDM-6-McKinney,%20Kenneth.pdf

However, in this situation, what we have done as well is retrofill the pringle switch and replace it with a LV circuit breaker with a trip unit and Arc-Flash maintenance switch. In one instance, our design has a remote control panel, located about 50' away from the room where it can be done.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883