It is currently Sun Aug 20, 2017 2:38 am
ekstra   ara
 Post subject: Table 410-3 Working Distances?
PostPosted: Tue Feb 24, 2015 1:01 pm
Offline
Hi,
Can someone explain the "T" values given in footnote 1 of Table 410-3 in the 2012 NESC. I am trying to find out if they have an impact on the distance from the arc as one might infer from the language. "...calculated using the MAD... subtracting two times the assumed arc gap length and using the following T values...."
Craig
 Post subject: Re: Table 410-3 Working Distances?
PostPosted: Wed Feb 25, 2015 5:52 am
Offline
T is the maximum anticipated per unit overvoltage factor.
PostPosted: Wed Feb 25, 2015 6:29 am
Offline
Hi Barry,
Thank you for the response and information. I would assume that if we want determine that other transient voltage levels should be used then we would need to analyze the system for such rather than using the default values.
Craig
PostPosted: Wed Feb 25, 2015 9:37 am
Offline
The T values were used in calculating the MAD, see Table 441-1. I expect the NESC T values and MADS should be conservative enough. In any case, you can only increase the MAD. Also note that if you use a larger MAD to calculate the distance to the arc, the result will be less conservative than what's in Table 410-3.
PostPosted: Wed Feb 25, 2015 10:12 am
Offline
Hi Steven,
Thanks for the added reference. I can see that T values are TOV values. and I understand what you are saying with regards to less conservative results coming from increased MAD's but I think that when using in the NESC option for analysis in my software (CYME) the working distance is determined form me based on voltage level and the default T values given in the NESC.
Craig
Who is online
Users browsing this forum: No registered users and 1 guest
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883
