acobb wrote:
For the high voltage overhead line work we have found 8 cal clothing to be more than adequate for most all cases. How does yours calculate? I also still believe for the line work portion, contact is still the most prevalent hazard.
For the 208 and 480 work, specifically padmounted or transclosure work, you can certainly have some extremely high IE available. We recommend no live work at this level whenever possible. No doubt that at 90 degree + temps the 20 cal or greater PPE with hard hat, face sheild, and gloves could easily create a greater opportunity for mistakes in a tight work area as well as the health issues you mentioned.
While taking the exception is an option, I would document the experience/reasoning (and the need to work it hot) well and hope for the best.
Thanks! We work in the desert SW and temperatures are usually above 100 degrees and often reach 115 or more in the summer. Heat exhaustion happens on a regular basis but arc flash is a pretty rare event. So we have to weigh our different hazards.
Yes an arc flash could be horrible but if we wear heavier PPE for that rare event, people will be dropping like flies. 8 cal is the best we can do and that is even questionable in mid summer. For pad mounted trfs and other ground work, we are also leaning towards 8 cal even though the calculated Ei is greater. If someone has the full suit on with the sun beating down, you are just about assured someone will be passing out.
We do try to de-energize when we can. The reduced PPE decisions are made with the input of many people.