 Post subject: Waist up protection only
PostPosted: Thu Nov 03, 2011 1:53 pm 

Joined: Thu Nov 03, 2011 1:43 pm
Posts: 2
Some utilities are only requiring FR rated shirts. They are allowing 100% cotton jeans without FR rating. The justification seems to be that "most" burns are from the waist up and the bucket protects from the waist down (where applicable of course). Comments?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 04, 2011 8:35 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
I see nothing in the 2007 code to support this. I suppose if the "detailed arc hazard analysis" of the 2012 code showed no hazard below the waist, this policy might be compliant. But a simple statement regarding most burns is not a detailed analysis. Also 2012 is not here yet.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 04, 2011 10:36 am 

Joined: Thu Nov 03, 2011 1:43 pm
Posts: 2
stevenal wrote:
I see nothing in the 2007 code to support this. I suppose if the "detailed arc hazard analysis" of the 2012 code showed no hazard below the waist, this policy might be compliant. But a simple statement regarding most burns is not a detailed analysis. Also 2012 is not here yet.


Totally agree, I haven't found any support for it either. Some of the larger IOUs do approach it this way however. I am trying to find out how they justify it since some of our clients have the "they do it why can't we" opinion of our recommendations. The 2012 code did hit the streets last month. New table for <1000V is very interesting.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 07, 2011 9:03 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
I didn't mean to say the 2012 code is not out yet, but that the year 2012 has not yet arrived. Therefore the 2012 code is not yet in effect. (and still won't be until Feb 1 or the date of jurisdion adoption.)


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883