ekstra   ara
 Post subject: kWh Meter Work
PostPosted: Tue Jan 06, 2009 8:43 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 862
Location: Rutland, VT
What is everyone doing for replacing/pulling/seal out of residential kWh meters?
Are you requiring a minimum of 4 cal clothing? What other PPE (face shield)?

What about the 480V metering that is not instrument PT fed?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jan 09, 2009 10:00 am 

Joined: Wed Dec 12, 2007 6:54 am
Posts: 9
The NESC Work Rules subcommittee is proposing new tables for section 41 for voltages below 1000 volts and currents below 50,000 amps.

Below is a summary of a relevant part of the proposed table

Self-contained meters /
Pad-mounted transformers / Panels and Cabinets

251 – 500 V
20 cal/cm^2(note 4)

4. Industry testing on 480V equipment indicates exposures for self-contained meters do not exceed 20 calories/cm2.