All -

What are you guys doing with respect to your UG manhole systems? Specifically, if you have calculated energies, what are you doing with PPE?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 01, 2009 12:06 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 576
http://standards.ieee.org/nesc/NESCIR557.pdf

Deenergize, mainly because of cable movement during a remote fault.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 01, 2009 2:35 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
One other issue to consider. Years ago I was in a small vault checking on some equipment when I noticed a portion of cable had "blown out" at some point allowing an energized 7,200 volt aluminum cable to be exposed. Somehow it was still operating. Didn't hang around very long!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 01, 2009 5:29 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 510
Location: New England
Enter manhole in HRC4. Check all cables with tic tracer. No live voltage found exit manhole and re-enter in HRC2.

De-energizing is often not practical. How many square miles of city is it acceptable to de-energize before inconvienence become infeasible?

Most manhole accidents to not occur because there was a conincidental fault on an adjacent cable. Most are from touch an energized conductor, by accident.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883