ekstra   ara
 Post subject: ETAP: Multifunction relay, Lockout Relay, Operating Times
PostPosted: Thu Jul 13, 2017 2:01 pm 
Offline

Joined: Thu Jul 06, 2017 9:19 am
Posts: 4
In ETAP (I'm using V16.1), where do I specify breaking opening delays caused by the multifunction relay or the lockout relay?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP: Multifunction relay, Lockout Relay, Operating Time
PostPosted: Mon Jul 17, 2017 11:21 am 
Offline

Joined: Fri Sep 10, 2010 7:48 pm
Posts: 14
Location: Idaho
You can go into the bus editor and the Arc Flash page and manually enter in a fault clearing time.