It is currently Sun Nov 08, 2026 8:48 am
 Post subject: Different Arc Flash Boundary in ArcPro and IEEE1584
PostPosted: Fri Sep 16, 2022 11:20 pm
Hello!
I am testing some calculations in ArcPro and IEEE1584.
I use the following inputs in ArcPro:
Voltage: 11kV
Current: 13.3kA
distance: 90cm
Arc gap: 15cm
duration: 0.25s
type: Enclosed, three phase
In ArcPro this gives an incident energy at working distance at 6.2 cal/cm2 and a Arc Flash Boundary at 205 cm. Comparing this with a calculation in IEEE1584 2012 (not the 2018 version) I get about the same energy 5.6 cal/cm2 but the Arc Flash Boundary 403 cm.
Very greatful for comments!
 Post subject: Re: Different Arc Flash Boundary in ArcPro and IEEE1584
PostPosted: Mon Sep 19, 2022 6:08 am
Does ArcPro use different bus configurations (horizontal, vertical, open air, etc.)?
Why not compare to IEEE-1548 2018? ..... out with the old and in with the new!!
I assume ArcPro is using the 2018 method, not 2012
PostPosted: Tue Sep 20, 2022 11:06 pm
Still it is strange that the energy is quite much the same but very different distance. Any other comments on this?
PostPosted: Wed Sep 21, 2022 7:18 am
They are two different models.
IEEE 1584 equations are empirically derived - conduct many tests, record data, develop equations.
ArcPro does not use the IEEE 1584 2002 or 2018 model. It is independent and from what I understand, ArcPro is a physics based model and I believe it was created quite some time ago. ArcPro is generally used above 15 kV mostly because no other models exist. IEEE 1584 is for use below 15kV.
PostPosted: Wed Sep 21, 2022 7:40 am
Arcpro doesn't use IEEE, and only the latest version considers electrode orientation. [url]https://www.kinectrics.com/Solutions/Pages/ARCPRO.aspx?creative=510930734634&keyword=arc%20flash%20software&matchtype=b&network=g&device=c&keyword=arc%20flash%20software&creative={creative]&gclid=EAIaIQobChMIqu7P_Y2m-gIVh2xvBB1a9QA7EAAYASAAEgIK_PD_BwE[/url]