 Post subject: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 8:19 am 

Joined: Wed Apr 06, 2011 2:20 pm
Posts: 21
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 8:42 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 606
I know nothing of ETAP, but many programs revert to the overly conservative Lee equations above 15 kV. ArcPro is one that does not.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 12:18 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 1:05 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 606
Jim Phillips (brainfiller) wrote:
abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault


Table lookup with interpolation? The Osha T&D Appendix E and NESC tables were derived using ArcPro. Better to go to the source in my opinion.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 1:45 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
stevenal wrote:
Jim Phillips (brainfiller) wrote:
abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault


Table lookup with interpolation? The Osha T&D Appendix E and NESC tables were derived using ArcPro. Better to go to the source in my opinion.


I've heard how but better to ask them directly.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883