It is currently Thu Jun 08, 2023 9:16 am
ekstra   ara
 Post subject: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 8:19 am
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .
 Post subject: Re: ETAP software capability for 34.5kV Power System
PostPosted: Mon Feb 06, 2023 8:42 am
I know nothing of ETAP, but many programs revert to the overly conservative Lee equations above 15 kV. ArcPro is one that does not.
PostPosted: Mon Feb 06, 2023 12:18 pm
Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.
https://etap.com/product/arcfault
PostPosted: Mon Feb 06, 2023 1:05 pm
Table lookup with interpolation? The Osha T&D Appendix E and NESC tables were derived using ArcPro. Better to go to the source in my opinion.
PostPosted: Mon Feb 06, 2023 1:45 pm
I've heard how but better to ask them directly.
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883