 Post subject: Arc Flash Protection Boundary in SKM
PostPosted: Wed Mar 23, 2011 2:43 pm 

Joined: Mon Jan 24, 2011 10:49 am
Posts: 3
Hi Everyone,

I'm using SKM to do the arc flash hazard analysis for a 208V Panelboard that is being fed by a small 75kVA transformer. I setup the arc flash option in SKM so that it will report a 1.2 cal/cm2 at this panelboard. Now I noticed that SKM uses an arc flash boundary of 18 inches for this default result. SKM also uses a clearing time of 2 seconds for this default result.

I was reading the arc flash protection boundary in NFPA-70E (2009) and what I understand from NFPA-70E is that we need to use a clearing time of 2 cycles (0.033 seconds), and an arc flash boundary of 4 feet for cases where detailed arc flash analysis are not performed.

My question is, do I need to change the clearing time and the arc flash boundary in SKM to be consistence with NFPA-70E? Thanks!

Viet


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 24, 2011 6:09 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1628
Location: Scottsdale, Arizona
Vietran wrote:
Hi Everyone,

I'm using SKM to do the arc flash hazard analysis for a 208V Panelboard that is being fed by a small 75kVA transformer. I setup the arc flash option in SKM so that it will report a 1.2 cal/cm2 at this panelboard. Now I noticed that SKM uses an arc flash boundary of 18 inches for this default result. SKM also uses a clearing time of 2 seconds for this default result.

I was reading the arc flash protection boundary in NFPA-70E (2009) and what I understand from NFPA-70E is that we need to use a clearing time of 2 cycles (0.033 seconds), and an arc flash boundary of 4 feet for cases where detailed arc flash analysis are not performed.

My question is, do I need to change the clearing time and the arc flash boundary in SKM to be consistence with NFPA-70E? Thanks!

Viet


The 2 second default is from IEEE 1584. That is the lowest duration cut off point listed in any standard. If you have a long clearing time, it is reasonable to cut of the duration at 2 seconds if there is room for escape - careful judgement must be used.

The 4 foot boundary default is subject to limitations of short circuit and clearing time not exceeding 1667 amp-seconds. It is not a completely random distance and the limitations must be considered.

I believe I understand why you are thinking about using 1.2 cal as a default, (208V circuit <125kVA transformer) However I am not sure I would do this. To me, listing an incident energy implies there was an analysis / calculations performed.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883