 Post subject: Arc Fault Damage Pictures Correlation to Arc Fault Calculations
PostPosted: Fri Nov 23, 2012 6:10 am
Group
Here is a link to another forum group that posted arc fault damage pictures and calcs.Thought it maybe of interest if you want to run your own software and calcs.
http://forums.mikeholt.com/showthread.php?t=149239
PostPosted: Mon Nov 26, 2012 9:19 am
ghostbuster wrote:
Group
It looks like the calculation method at this link is very old, from the 1997 Doughty/Neal paper. They should really be using the IEEE 1584 calculations. I've seen the forum host link to a few articles with the IEEE 1584 method. Also there is book on the subject that shows up in the forum sponsor box on the right.