| Arc Fault Damage Pictures Correlation to Arc Fault Calculations https://brainfiller.com/arcflashforum/viewtopic.php?f=15&t=2542 |
Page 1 of 1 |
| Author: | ghostbuster [ Fri Nov 23, 2012 6:10 am ] |
| Post subject: | Arc Fault Damage Pictures Correlation to Arc Fault Calculations |
Group Here is a link to another forum group that posted arc fault damage pictures and calcs.Thought it maybe of interest if you want to run your own software and calcs. http://forums.mikeholt.com/showthread.php?t=149239 |
| Author: | JoeB [ Mon Nov 26, 2012 9:19 am ] |
| Post subject: | |
ghostbuster wrote: Group Here is a link to another forum group that posted arc fault damage pictures and calcs.Thought it maybe of interest if you want to run your own software and calcs. http://forums.mikeholt.com/showthread.php?t=149239 It looks like the calculation method at this link is very old, from the 1997 Doughty/Neal paper. They should really be using the IEEE 1584 calculations. I've seen the forum host link to a few articles with the IEEE 1584 method. Also there is book on the subject that shows up in the forum sponsor box on the right. |