 Post subject: What is Arc Flash event ?
PostPosted: Thu Oct 22, 2015 9:44 am 

Joined: Wed Apr 06, 2011 2:20 pm
Posts: 16
Recently , we have three phase Non-Segregated bus fault and it melted the bus. I am little bit confused about what is the meaning of Arc Flash fault. When we do the Arc Flash analysis then we consider the Cubical door is opened and someone is going to change the state of the protective device. But if the door is closed and nobody is changing the state of the protection device and fault happens.Can we say this is Arc Flash event? If yes then we have to wear Arc Flash PPE as while you are close by Electrical Equipment as you do not know when Arc Flash event may happen. Can anyone describe about Arc Flash event?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What is Arc Flash event ?
PostPosted: Mon Oct 26, 2015 10:46 am 

Joined: Fri Apr 01, 2011 5:00 pm
Posts: 5
Location: Minnetonka, MN
Please look at the definition of an arc flash in Art 100 of 70E - a dangerous condition associated with the possible release of energy caused by an electric arc. An Arc Flash does not necessarily depend upon human interaction or position of the electrical equipment (enclosed, guarded, or wide open-that is "exposed" . This could be why the 70E-2015 definition of normal operations as not requiring Arc Rated PPE may be misleading. Arc flashes can happen with just equipment insulation failures, and without human intervention/interaction. You must approach energized electrical equipment with the understanding that a risk assessment (as defined by 70E) is realistically required before entering into the shock and arc flash boundaries.

_________________
Steven T Rasmussen CESCP
Zone Safety Rep


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What is Arc Flash event ?
PostPosted: Mon Oct 26, 2015 7:29 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
Arcing faults can happen at any time, and arcing faults are different from bolted faults. Just because bus is not segregated makes no difference. Segregated bus just theoretically limits it to line-neutral faults but I've seen line-line still and since especially the tubular kind is almost impossible to inspect, its worse. The difference is that doing certain activities around electrical gear significantly increases the likelihood of a fault.

In the case of busducts, they are notorious for joint failures because there are so many joints, bus can failures during stabbing operations, and faults due to environmentalcontamination.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883