| Author |
Message |
mcgee9t2
Post subject: X/R Ratio Posted: Fri Sep 13, 2019 2:19 am |
Hoping you may be able to help.
I have two models, (the models need to be kept seperate for confidentiality), lets call them model A and B.
I am currently running arc flash calculations on Model B (have previously completed model A).
Model B is fed from a substation on model A, as such i have taken the fault level at the relevent sub in model A and used as a utility in model B.
i am unsure how to find the X/R ratio for the sub so i can transfer into the utility.
i have tried creating an X/R datablock and imported X/R LL, X/R Neg, X/R Pos, X/R SLG & X/R Zero. however all display 0.
even when i put a utility with an X/R of 8 onto a bus (i.e. no cabling or anything, therefore the X/R at the bus should be 8) it displays 0.
am i missing something? is there an easy way for me to find out the X/R ratio at the switchroom so that i can transfer into the utility of Model B
much appreciated for any info.
| Top |
JBD
Post subject: Re: X/R Ratio Posted: Fri Sep 13, 2019 6:12 am |
Joined: Mon Jan 18, 2010 11:35 am Posts: 617 Location: Wisconsin
It may depend on your software. But for these types of projects, I usually look at the Short Circuit output report to find the X/R. I know it hows up there on both PTW and ETAP.
| Top |
mcgee9t2
Post subject: Re: X/R Ratio Posted: Fri Sep 13, 2019 6:41 am |
found it, i was looking at the wrong datablock i needed iec909 XoverR Neg/Pos/Zero
| Top |
Page 1 of 1
[ 3 posts ] |
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot post attachments in this forum