| Arc Flash Forum https://brainfiller.com/arcflashforum/ |
|
| SKM Unbalanced/Single Phase Module https://brainfiller.com/arcflashforum/viewtopic.php?f=15&t=5226 |
Page 1 of 1 |
| Author: | makoester1 [ Mon Dec 16, 2019 9:02 am ] |
| Post subject: | SKM Unbalanced/Single Phase Module |
Good Morning All, I am curious if anyone utilizes the SKM Unbalanced/Single Phase Module? I have several instances with single phase loads and evaluating adding this module to our current license. I am wondering if anyone could share their opinions/experiences regarding this module? Thanks |
|
| Author: | Robertefuhr [ Mon Jan 06, 2020 1:53 pm ] |
| Post subject: | Re: SKM Unbalanced/Single Phase Module |
Yes, we use the Unbalanced/Single Phase SKM module. It works really well. However, if you are trying to calculate the AF energy for a single phase system less than 15 kV then you will be out of luck. The SKM AF module uses IEEE-1584 which will calculate AF energy only for a 3 phase balanced system. For open air equipment, you can use ArcPro. |
|
| Page 1 of 1 | All times are UTC - 7 hours |