Author:  abk453 [ Mon Feb 06, 2023 8:19 am ]
Post subject:  ETAP software capability for 34.5kV Power System

Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Author:  stevenal [ Mon Feb 06, 2023 8:42 am ]
Post subject:  Re: ETAP software capability for 34.5kV Power System

I know nothing of ETAP, but many programs revert to the overly conservative Lee equations above 15 kV. ArcPro is one that does not.

Author:  Jim Phillips (brainfiller) [ Mon Feb 06, 2023 12:18 pm ]
Post subject:  Re: ETAP software capability for 34.5kV Power System

abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault

Author:  stevenal [ Mon Feb 06, 2023 1:05 pm ]
Post subject:  Re: ETAP software capability for 34.5kV Power System

Jim Phillips (brainfiller) wrote:
abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault


Table lookup with interpolation? The Osha T&D Appendix E and NESC tables were derived using ArcPro. Better to go to the source in my opinion.

Author:  Jim Phillips (brainfiller) [ Mon Feb 06, 2023 1:45 pm ]
Post subject:  Re: ETAP software capability for 34.5kV Power System

stevenal wrote:
Jim Phillips (brainfiller) wrote:
abk453 wrote:
Can ETAP be utilized for 34.5kV power system Arc Flash analysis as ETAP follows IEEE1584 which is only limited to 15kV . If not then which software and standard is suitable for 34.5kV .

Yes, above 15 kV they base it on OSHA 1910.269 Appendix E and NESC-C2-2012 to 2017. Link is below.

https://etap.com/product/arcfault


Table lookup with interpolation? The Osha T&D Appendix E and NESC tables were derived using ArcPro. Better to go to the source in my opinion.


I've heard how but better to ask them directly.