Not enough information to answer as I'd have to see the protection scheme but my question is, what type of transformer is this and what are the voltages? Are you actually labeling it? What are you using for box size or is this a substation transformer with terminations in open air? What are you using for bus gaps?
I seen others blindly model transformers with the default "PNL" or "SWG" VCB without accounting for the actual enclosure size or bus gaps or if it is in the air and not a box etc. and the results are not reality.
Voltage may also be an issue and SKM might not be the right tool, or it may be.
Again, not enough information.
Also, need to make sure you have the transformer data completely input accurately.
https://www.skm.com/applicationguides5.htmlAttachment: