Jake Kingsbury
Post subject: Unreasonable current during study Posted: Fri Jun 26, 2026 11:26 am |
| Attachments: |
| Top |
bbaumer
Post subject: Re: Unreasonable current during study Posted: Sat Jun 27, 2026 8:22 am |
| Arc Level |
Couple of questions:
_________________ Retired but I might visit once in awhile
| Top |
Win Engineer
Post subject: Re: Unreasonable current during study Posted: Fri Jul 10, 2026 9:11 am |
Use the Branch fault Current data block and see what fault current you have flowing through the system. I had a model years ago that was yielding some ridiculous fault currents on a 208V system and discovered that a bunch of 10HP motors had been entered at 10,000HP. You can imagine at 208V the fault contribution from the motors! That data block showed me the fault current coming back into the bus was really high and pointed me straight to the issue.
| Top |