Charles R. Miller wrote:
I am currently writing a series titled "Sizing Conductors" in Electrical Contractor Magazine. Find the conductor size in this example before it is published in the September issue.
"What size THHN copper conductors are required to supply a branch circuit under the following conditions? The load will be a 39-ampere, continuous load. These branch-circuit conductors will be in a raceway. There will be a total of eight current-carrying conductors and an equipment grounding conductor in this raceway. The terminations on both ends are rated at least 75°C. The maximum ambient temperature will be 40°C."
Just to clarify so that no looks for 90 Deg C equipment terminations. Your comment "rated at least 75 deg C", to the best of my knowledge there is no equipment rated greater than 75 deg C, terminations yes, equipment no. It is even worst on UL508 listings, most control is 60 Deg C.