 Post subject: Series Ratings
PostPosted: Thu Jan 18, 2024 9:23 am 

Joined: Wed Jan 17, 2024 8:34 pm
Posts: 3
Hello all!

I have a situation where a LV panelboard is rated for 10kAIC and the short circuit eval indicates it could see up to 15kAIC for a fault condition. The feeder breakers in the panel are all the same and also rated at 10kAIC, however the feeders series rate with the main at 65kAIC. My question is: does the series rating of the OCPD's also create a series rating of 65kAIC for the panelboard? I think the answer is no. My understanding is that the series combinations are tested by the breaker manufacturer but if the panel is rated at 10kAIC then that shouldn't change based on the series ratings of the breakers. I don't see anything in the NEC that specifically talks about the panelboard in this situation.

Any wisdom would be greatly appreciated.

Thanks all!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Ratings
PostPosted: Thu Jan 18, 2024 10:34 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 374
Location: Indiana
https://www.se.com/us/en/faqs/FA236819/ ... he%20panel.

_________________
SKM jockey for hire
PE in 16 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Ratings
PostPosted: Thu Jan 18, 2024 11:35 am 

Joined: Wed Jan 17, 2024 8:34 pm
Posts: 3
Thanks!!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883