ekstra   ara
 Post subject: arc flash boundary markings
PostPosted: Wed Mar 30, 2016 3:53 am 

Joined: Thu Jun 11, 2015 10:54 pm
Posts: 1
Dear All,

I would like to ask one important issue related to Arc flash boundary markings in the industries like we have to mark the boundary for wall mounted DB's or not (which can be in Office area). If yes, then what would be the distance in mm or feet. Please advice.
Thanks,


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash boundary markings
PostPosted: Wed Mar 30, 2016 6:30 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
yasharora1988 wrote:
Dear All,

I would like to ask one important issue related to Arc flash boundary markings in the industries like we have to mark the boundary for wall mounted DB's or not (which can be in Office area). If yes, then what would be the distance in mm or feet. Please advice.
Thanks,


Your arc flash boundary is a calculated value for each piece of equipment based on your arc flash study.

If you don't have a study, you would use the distances listed in NFPA 70E Table 130.7(C)(15)(A)(b).


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash boundary markings
PostPosted: Wed Mar 30, 2016 12:17 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 826
Location: Rutland, VT
Additionally NFPA 70E-2015 requires the arc flash boundary to be on the label. The only boundaries I have seen actually marked out are the ones in front of electrical panels to keep people from storing stuff in front of them.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash boundary markings
PostPosted: Thu Mar 31, 2016 6:31 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
NEC has a suggested list of what has to be marked but keep in mind that the list is a guideline and should not be read as an absolute rule. The key is whether or not the equipment is accessed for maintenance "frequently" which is generally considered to be more than once a year. For instance if you have equipment that is rarely (cycle is more than 12 months) serviced and not used as say a primary disconnect for servicing other equipment, then it would not have a label. This would also mean that some things that are not on the NEC guideline would qualify.

In addition, NEC does not specify that it has to be marked directly on the equipment. 70E gives specific requirements for labels but does not have direct regulatory authority. So some plants have a practice where if it is not labelled, there is an assumed value. This is usually (but not always) 1.2 cal/cm2. Others follow the above example and the rule is that when in doubt, seek out the maintainer of the arc flash study (engineer) to find out the value to use for rarely used equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash boundary markings
PostPosted: Fri Apr 01, 2016 4:43 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
Personally I don't like the assume "category 0" (<1.2 cal/cm2) because of the possibility of missing something. The industrial plant I am working in now has missing labels on equipment I know is greater than 1.2 cal/cm2. I'd rather the worker come to me and I can look up the arc flash value (and as soon as I get a printer I can print them a label to put on the equipment.)


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883