It is currently Wed Oct 28, 2026 10:15 pm
 Post subject: arc flash enclosure
PostPosted: Wed Jan 06, 2021 7:24 pm
I have a client whom recently had some electrical work done. The contractor installed enclosed breaker (480V, 3-phase, 400A) in an enclosure of which the cover is secured with bolts and nuts. The Owner is wondering what type of enclosure this is and why?
Best I can tell it is GE arc flash rated enclosure. the front cover is literally secured with about 5 threaded bolts w/nuts on each side.
Anyone know what is the purpose of such an enclosure?
 Post subject: Re: arc flash enclosure
PostPosted: Thu Jan 07, 2021 2:45 pm
sounds like he just used an enclosure for a stand alone breaker. Not unusual as I have seen that type of setup before in lieu of a fused disconnect switch. I have also seen that type of setup used separate from an MLO MCC to reduce the arc flash at the MCC.
PostPosted: Thu Jan 07, 2021 6:12 pm
If the cover requires tools to open and access and operate the breaker, it sounds like it may be a code violation.
PostPosted: Mon Jan 11, 2021 8:38 am
It is possible that the enclosure is attempting to do something similar to enclosures used in Classified Area i.e. Class I Division1 by venting and cooling any any gases heated during an arc flash event via the gap between the cover and the enclosure box while maintaining the structural integrity of the enclosure.
PostPosted: Mon Jan 11, 2021 9:06 am
Yes, could be hazardous location enclosure. Is there nameplate? Can you post a photo?
Alan Lehman